Concorde Fuel pressure

Discussion in 'Concorde' started by Smitty, Oct 25, 2006.

  1. Smitty

    Smitty Guest

    I have a 95 Concorde that is starting to take longer to crank than it
    should. I suspect the fuel pressure regulator. I was going to pop one in as
    a guess until I saw what a job it was. Looks like the intake manifold or
    what ever they call it now days has to come off. Is this correct? (I've
    gotta find a manual for it one of these days). Is there something else
    (easier) I should try before I take this route?
    Thanks
    Smitty on the frozen tundra of Minnesota
     
    Smitty, Oct 25, 2006
    #1
  2. Smitty

    Bill Putney Guest

    More than likely, one of two things is happening:
    (1) One or more injectors is leaky - when the car sits with engine off,
    for a few hours, the fuel rail empties out into the cylinder or
    cylinders with the leaky injectors. When you go to start it back up,
    the fuel pump has to first re-fill the fuel rail before it can supply
    and pressurize the injectors.
    (2) Check valve back at fuel pump is leaky - fuel lines empty out with
    similar results - pump has to refill system before cylinders see fuel
    from injectors.

    I don't know about 1st gen LH's, but on 2nd gens, the way to prove that
    either (1) or (2) is happening is to turn key to run (not start) for a
    couple of seconds, then to off, then again to run for a couple of
    seconds, then to off, then to start - if it starts on the first try
    after doing that, then either (1) or (2) is the problem. The reason is
    that the fuel pump shuts off after a second or so if it does not detect
    engine start. By cycling the key a few times, you let the pump run for
    several of those second or so bursts - enough run time to refill the
    rail. If you try to start without cycling the key, the single burst of
    pump run time is not enough.

    Pressure regulator for 2nd gens is in the fuel tank (part of sender/pump
    assembly) - 1st gens are probably like that too - but not sure. But
    that is probably not the problem - see (1) and (2) above.

    Bill Putney
    (To reply by e-mail, replace the last letter of the alphabet in my
    address with the letter 'x')
     
    Bill Putney, Oct 25, 2006
    #2
  3. Smitty

    Steve Guest

    The upper plenum has to come off (I'm assuming a 3.5L engine). Its not a
    big job, really. A quick check is to pull the vacuum line off the fuel
    pressure regulator and see if fuel comes out, indicating a leaky
    diaphragm. Been there, done that- it caused fuel pressure leak-down over
    a few hours, followed by longer than normal cranking on the next restart
    to rebuild the fuel pressure and clear the leaked of fuel out of the
    vacuum lines.
     
    Steve, Oct 25, 2006
    #3
  4. Smitty

    Steve Guest

    Nope, that's one of the things they cheaped out on the second gens.
    First gens have a full recirculation type fuel loop. The pressure
    regulator is in the fuel rail, and fuel "bled off" by the regulator
    returns to the tank, keeping cool fuel at the injectors at all times. I
    think the purported reason (rather than just admitting "we're cheap" ;-)
    for the change was that a recirculation system causes the fuel in the
    tank to become a few degrees warmer over time, and thus increases
    evaporative emissions. But the cool fuel at the injectors is sure nice
    for performance and consistency.
     
    Steve, Oct 25, 2006
    #4
  5. Smitty

    maxpower Guest

    More then likely the fuel pump check valve is bad causing the fuel to drain
    back to the tank as Bill said. The injector(s) could also cause this problem
    but if that were the case you would have a hard time starting this vehicle
    after a hot soak.

    Glenn Beasley
    Chrysler Tech
     
    maxpower, Oct 25, 2006
    #5
  6. Smitty

    Bill Putney Guest

    OK - I stand corrected. Thanks.

    Bill Putney
    (To reply by e-mail, replace the last letter of the alphabet in my
    address with the letter 'x')
     
    Bill Putney, Oct 26, 2006
    #6
  7. Smitty

    maxpower Guest

    The regulator is under the intake on this model. If the regulator is bad
    there would still be fuel from the pump to the fuel rail The pump still has
    a check valve built into it to prevent fuel from draining back to the tank.

    As far as the fuel loop goes you have it backwards or Im just reading it
    wrong. when the fuel regulator was at the intake it caused the fuel in the
    tank to heat up, causing higher emissions. By having the fuel pressure
    regulator on the pump in the tank, it keeps the fuel at a cooler
    temperature. This is done by not having the fuel heated up by the exhaust
    and under hood temperature and then going back to the tank

    Glenn Beasley
    Chrysler Tech
     
    maxpower, Oct 26, 2006
    #7
  8. Smitty

    Steve Guest

    Right (allegedly).
    The fuel in the TANK stays cooler without a loop, but the fuel AT THE
    INJECTORS is much hotter, because intsead of continuously circulating it
    just flows slowly through the rail warming up to the temperature of the
    cylinder head or injector that its flowing into. That's the whole reason
    that the carbureted Hemi and 440 Magnum cars of the 60s had a similar
    fuel loop that pumped excess fuel from the filter back to the tank, so
    that the fuel headed to the carb would be as cool as possible to prevent
    vapor lock. Its not as big a deal on high pressure fuel injection, but
    keeping the fuel cooler is always a little better for engine performance
    and consistent mixture control.
     
    Steve, Oct 26, 2006
    #8
  9. Smitty

    Bill Putney Guest

    Glenn - I'm thinking that the fuel mass in the engine compartment
    environment (in the lines and fuel rail) is a *lot* less than the volume
    in the tank - therefore, with a given number of calories absorbed by the
    lines and rail, it's temperature rise without the full loop circulation
    will be a *lot* higher than the rise in the whole tank (from the heated
    fuel returning to the tank), plus heat dumped over that huge volume back
    at the tank will also be dissipated at a moderate enough rate into the
    ambient due to the large surface area if the tank acting as a radiator -
    the net result of the full loop circulation will be lower temperature at
    the point of injection into the plenum.

    Bill Putney
    (To reply by e-mail, replace the last letter of the alphabet in my
    address with the letter 'x')
     
    Bill Putney, Oct 27, 2006
    #9
  10. Smitty

    DeserTBoB Guest

    Possessive: "ITS"
    Contractive form of the third person "to be": "IT'S"

    GOTCHA!
    Putney's right here. I have an exact same, but much larger, model I
    dealt with when retrofitting emergency diesel and gas turbine
    generator fuel tanks back in the '90s.

    Most original installations of these were much like the older FI
    system....diesel or JP-4 would be pumped into a day tank, the engine
    would take what it needed from there, and return excess fuel from the
    pump or rail directly to the fuel tank through a separate return line.
    Contractors, looking to make a extra bucks on loosely spec'd "design
    and build" contracts, would replace the tank with a double wall
    replacement (usually 5K gallons or more) and double wall piping, but
    only a supply line would be provided, dumping the heated excess from
    the engine of the generator set(s) into the day tank. The problem was
    that the diesel would become dangerously hot after hours of operation,
    the amount varying from model to model and by, of course, capacity.

    In the projects of which I was in charge, I demanded that a double
    walled return line be added to the spec to prevent this. A 10K tank
    filled with #2 diesel, feeding a 750 KW generator set running at 80%
    load (Cummins VT-38000/Marathon alternator), with a ground temperature
    of 19°C, would heat up 4°C after 8 hours operation. However, one
    "single line" installation, using the same load factor but on a 16V71T
    Detroit Diesel, would heat the fuel in a 100 gallon day tank up to
    almost 40°C in half the time period. Detroits run a common loop
    rail/unit injector system on top of the heads, whereas the Cummins
    used a PT pump with less exposure of the fuel in the cylinder head
    area, so there was a little more heat transfer from the Detroit, but
    the case for the dedicated return line was made, and the company's bid
    specs were changed to include same.

    (Note that I also wasn't stupid enough to use a Detroit Diesel for a
    generator set engine! What a disaster, but the middle manager
    "injuneers" at AT&T prevailed on that one. One on them was later
    allowed to "retire" after rather large kickbacks involving the
    supplier were uncovered and the IRS started investigating, and AT&T
    got a little skittish having IRS investigators showing up back in New
    Jersey.)

    I would imagine the same sort of problems with hot fuel due to having
    the regulator/return in the tank in a gasoline powered car would be
    similar. The concern of heating of the volatiles in the fuel tank is
    a non-starter, as well, since the evap system would take care of that
    at start-up. I think the reason for this change was one that Frank
    Zappa would full appreciate: "cheapness."
     
    DeserTBoB, Oct 27, 2006
    #10
  11. Smitty

    maxpower Guest

    Thats true

    therefore, with a given number of calories absorbed by the
    Thats true too, but who cares? The higher the fuel pressure the less
    chances of fuel foaming and all that good stuff. But circulating the fuel
    back to the tank causes higher fuel temperatures in the tank. thus higher
    hydrocarbons.

    (from the heated
    Once again, who cares what the temp is at the injectors???? The ambient temp
    and coolant temp sensor will adjust for all that. The high pressure fuel
    pump will eliminate any fuel foaming/vapor lock.
    I don't know what all that mumbo jumbo means that you type but
    since 1998, all fuel systems were designed to be returnless to minimize heat
    in the tank, which leads to excessive hydrocarbons
     
    maxpower, Oct 27, 2006
    #11
  12. Smitty

    Bill Putney Guest

    Yep. I'm usually pretty good about "it's" and "its". I was running
    late for work and in too much of a hurry on that one. Check the post
    time - I have to be out the door no later than 6:41 in order to not be
    late to work. That's my story and I'm sticking to it.

    I still can't keep straight about precede and proceed. If precede is
    spelled like that, why is proceed spelled like it is - and if it's (ahh
    - got it right) proceed, why is it "procedure", yet it's "preceding" and
    not "preceeding"!?

    Bill Putney
    (To reply by e-mail, replace the last letter of the alphabet in my
    address with the letter 'x')
     
    Bill Putney, Oct 28, 2006
    #12
  13. Smitty

    DeserTBoB Guest

    Because, like New Englandese pronunciation, there are NO rules in
    English...except when there ARE some!
     
    DeserTBoB, Oct 28, 2006
    #13
  14. Smitty

    cavedweller Guest

    Yes, your usually pretty good about keeping you're "itses" write but
    you may have been superseded.... ;) (ducking).
     
    cavedweller, Oct 28, 2006
    #14
  15. Smitty

    Bill Putney Guest

    Hey - like the Indian guy in "Short Circuit" said: With friends like
    you, who needs enemas!? :)

    Bill Putney
    (To reply by e-mail, replace the last letter of the alphabet in my
    address with the letter 'x')
     
    Bill Putney, Oct 28, 2006
    #15
  16. Smitty

    Bill Putney Guest

    Many people don't know this, but Teddy Roosevelt set up a commission to
    standardize spelling for the nation. I guess for those particular words
    they may have deferred to common usage spelling in the legal system or
    something rather than some consistent (and arguably arbitrary) rule.

    Bill Putney
    (To reply by e-mail, replace the last letter of the alphabet in my
    address with the letter 'x')
     
    Bill Putney, Oct 28, 2006
    #16
  17. Smitty

    Smitty Guest

    If we get some warm weather I'm going to try some of these tips. Since this
    one has the pressure regulator buried under the intake I'm thinking it is a
    first generation eh?
    Thanks a lot.
    Smitty
     
    Smitty, Oct 29, 2006
    #17
  18. Smitty

    Bill Putney Guest

    Correct. For LH cars (Intrepid, Concorde, LHS), anything prior to '98
    is first gen. (there was no LH 1st gen. 300M).

    Bill Putney
    (To reply by e-mail, replace the last letter of the alphabet in my
    address with the letter 'x')
     
    Bill Putney, Oct 29, 2006
    #18
  19. Smitty

    maxpower Guest

    If this is the 3.5 engine don't forget there was a recall out to replace
    the injector o-rings and replace the cracked fuel rail or reinforcing it.
    Has that been done to your vehicle yet? (assuming 3.5).

    Glenn Beasley
    Chrysler Tech
     
    maxpower, Oct 29, 2006
    #19
  20. Smitty

    maxpower Guest

    If this is the 3.5 engine don't forget there was a recall out to replace
    the injector o-rings and replace the cracked fuel rail or reinforcing it.
    Has that been done to your vehicle yet? (assuming 3.5).

    Glenn Beasley
    Chrysler Tech
     
    maxpower, Oct 29, 2006
    #20
Ask a Question

Want to reply to this thread or ask your own question?

You'll need to choose a username for the site, which only take a couple of moments (here). After that, you can post your question and our members will help you out.